r/ElectricalHelp • u/aryzarrin • 1d ago
Parallel Arc Fault
Hello Electrician brain trust!
Let me start this post by saying that the breaker is off, I’ve contacted an electrician and am waiting for a callback to schedule an appointment. No burning smell, and none of the outlets were warm on the affected circuit.
We are in Maryland and currently subject to this Nor’easter. Power went out briefly close to the top of the hour and since it restored the breaker to my “man cave” has been tripped.
I went to flip it back on and noticed that the AF LED was blinking about once every second. The breaker is Leviton brand and their LED diagnosis KB said this is indicative of a Parallel Arc Fault, and to contact and electrician.
I unplugged all the devices, and tried once more (I know, sorry I wasn’t supposed to) just to make sure and the behavior stayed the same.
Any more troubleshooting / investigating I can do? The house is a new build about a year old, so if it’s an issue with the original wiring install I fully plan to have them address the issue and cover any costs incurred.
Appreciate the insight, and I hope you all have a wonderful Thanksgiving! I’m sure a good portion of you along the east coast might be busy though…
3
u/RedRoosterOICU812 1d ago edited 1d ago
Since you're experiencing heavy weather, do you have an outdoor receptacle on your man cave circuit? If it got saturated with ice, snow, or water that could be your issue. Also if that receptacle outside is a ground fault receptacle, that could be your issue.
Check and see if you have an outdoor receptacle or light for that matter that became damaged or saturated in the storm. Just a power outage should not trigger a breaker malfunction. If you called me out that would be the first thing I would check for. The next thing I would check would be the breaker itself. I would swap a working breaker for your malfunctioning one and see if that cleared it up.
1
u/Davis1377 1d ago
I believe the blinking is telling you what it tripped for last. These types of breakers are very sensitive to computers, electric fans and stuff that can trip them very easy.
1
u/Unique_Acadia_2099 23h ago
Parallel arc faults means something is arcing from line to ground, as opposed to jumping across a gap in a broken wire or loose connection. It’s basically the same as a Ground Fault, except that arcing faults can have enough resistance in them that a GFCI will not trip. A parallel AFCI is not looking at the AMOUNT of current, but rather the PATTERN of it that indicates an arc situation is taking place.
Yes, this could, in older generations, be “fooled” by electronic power supplies because of the “non-linear” way they draw current. So IF you recently plugged something new into that circuit, unplug it and see if it resets. If it does, that’s the problem. But that issue has (with some exceptions) been mostly solved over the years, so unless you have an AFCI breaker that has been installed for - decode or more, that’s unlikely.
One straggler in solving that issue had been Siemens, who got sued over it in 2022, but even then they tweaked their algorithm in 2023, and since then I haven’t seen it happening still.
But given the weather conditions for you, it’s far more likely that something is leaking water into an electrical box and causing a short.
1
u/DoctorCAD 2h ago
Arc fault breakers are notorious for failing. I'd simply get another one and replace it.