r/ecobee • • 16h ago

Humidifier Hack

Post image
15 Upvotes

I got an Ecobee in the summer, and never used the humidifier but in the fall and winter I have to where I live.

Anyway, everything looked to be working correctly, I even replaced the evaporative panel but humidity was not coming up beyond 20-27%. Not once in 6 weeks did it go over 30%, with the last recorded at the start of October.

I contacted AprilAire support and they told me that it's possible my furnace run time is too short to bring up humidity, and the ecobee will only send notice to an evaporative humidifier to turn on during heating.

So, even though their humidifier (500 series) is designed to run with hot air I COULD try it on cold air. To do this, he advised I set my Ecobee to "steam" humidifier instead, which will cause it to turn on the fan and humidifier at the same time.

Lo and behold... it worked! Since turning it on the humidity rose steadily and it's literally night and day for the last 72 hours with my house up to a much more comfortable 34%!


r/ecobee • • 2h ago

Question Ecobee preheating or incorrectly reading wrong sensors

1 Upvotes

I have an ecobee thermostat and one remote sensor. Heating and cooling smart recovery are already disabled, which I did long ago to stop precooling. Now that I recently switched to heat, I seem to have a preheating issue.

Eco+ schedule assistance and adjustment for humidity are on, set at basic savings. This is the only remaining setting I can think of that might be the cause, but it's not an issue when cooling so idk why it would be with heating. I do not see the alert that eco+ is running when I have this issue though, and the description of these settings on ecobee's site doesn't explain this behavior. Smart home/away is off. I fully control the temp and have not given control to my utility company.

At 12 AM the schedule should use only the remote sensor with a set temp of 65. Immediately prior to that time the schedule should use only the thermostat with a set temp of 71. Follow me setting is off.

About 25 mins prior to 12 AM and with an individual thermostat reading already at 71 my heat is turning on. Both the thermostat and remote sensor are white in the app, so it's averaging the temp of both instead of using only the thermostat as it should. The remote sensor being in a cold room is dropping the avg, and the heat stays on until both rooms end up well above their individual set temps making both rooms uncomfortable even after I switch to the new schedule setting at 12 AM.

My schedule and settings aren't ever set up to use the avg of both sensors so this is an error. How do I put a stop to this?


r/ecobee • • 12h ago

Upgrading PRO1 IAQ T701

Thumbnail gallery
1 Upvotes

r/ecobee • • 17h ago

Ecobee help

0 Upvotes

Hello, looking for some Ecobee help that I cannot seem to get to the bottom of. I recently bought a house with an Ecobee installed. The temp differential seems to swing one way in the summer around +4 and in the fall so far more like 0. In Florida where we have cold nights and warm days it’s very difficult to get the settings dialed in. Anyone have a similar experience or any suggestions?


r/ecobee • • 18h ago

Question Furnace turns on stage 2 before Aux Stage 2 Temp Delta is reached

1 Upvotes

I have a winter setup with my heat pump and furnace, where I would like the furnace to run on low heat most of the time (it's a 2-stage furnace). I have an Ecobee 6, and I set the thresholds to the following:

Compressor Stage 2 Temperature Delta: 0.5C

Compressor to Aux Temperature Delta: 1C

Aux Stage 2 Temp Delta: 5.5C

Aux Stage 1 Max Runtime: Auto

I set the furnace back during the night by 5C, and it usually cools down somewhere between 3C and 5C at this time of year. I was hoping with my above thresholds, that the furnace would always turn on at stage 1, never stage 2. It does this on warmer nights, but not on the coldest.

From my testing, I have determined that the furnace will use stage 2 (high heat) when the temperature differential is somewhere between 4.3C and 4.8C. In other words, not even close to the 5.5C limit I set.

Does anyone know why this is? I can't set the limit any higher than 5.5C, since that's the max. (I presume internally the limit is 10F, but the furnace goes to stage 2 at around 8.5F difference.)

I know it's not a big deal, but I really don't like high heat unless I really need it (like when it's -30C outside.) I can work-around the issue by using different comfort profiles to slowly ramp up the temperature in the morning, but that has some downsides.


r/ecobee • • 1d ago

36k BTU Mitsubishi hyper heat/ air handler thermostat question

Post image
1 Upvotes

r/ecobee • • 1d ago

Configuration Ecobee premium vs ecobee lite contractor version

0 Upvotes

Im about to have a new furnace installed.and decided to upgrade my smart thermostat (nest from 2018).

The HVAC company doing the installation offered to put the ecobee lite STATE7P. However, there a bunch of rebates available that I can stack on black Friday sales at the ecobee store.

Will I be losing any capability going with the premium?


r/ecobee • • 2d ago

Question Variance in Temp Set

0 Upvotes

I have my ecobee set at heat at 63 degrees. Sometimes the heat doesn’t come on until the temperature reading is 59. Why is there such a variance between what I want the temperature to be and when the heat comes on? I don’t have any other temperature sensors, just the thermostat.


r/ecobee • • 2d ago

Resolved Need help with PEK install

Thumbnail
gallery
0 Upvotes

I’m having trouble figuring out how to correctly install the PEK, mainly confused on the 2 red wires, one connected to R and the other connected to Y/Y2.

The blue wire above the red ones is also connected to Y/Y2, and that is the one connected to Y on my thermostat.

Then there are 2 white wires. One connected to W, the other connected to C, there is only one white wire connected to W on my thermostat, there isn’t anything connected to C.


r/ecobee • • 2d ago

Other Any way to fix this?

Post image
1 Upvotes

Every time the heat kicks on, the bedroom will get abnormally hot. (It’s closer to the furnace than the rest of the house is) the return air is in the other side of the house from the bedroom, but it still gets about 10 degrees warmer while the heat is on. It evens out around the middle of the day since it doesn’t run as much, but still!

It seems I’m at a constant battle of trying to keep the bedroom cool enough to sleep in while keeping the rest of the house at a reasonable warm temp during the night.

Any way to fix?


r/ecobee • • 2d ago

Furnace “malfunctions” at night

0 Upvotes

Four times now over the past two months, I’ve received an email warning about how my furnace may be broken because Ecobee has been asking for heat, yet the house is dropping degrees.

This only happens at night—the first time I called HVAC and they could see nothing wrong. At this point, my assumption is with the settings. What might be triggering this? It seems to wake up once “sleep” setting are over.

Currently hundreds of miles away from my home getting a “there’s a problem with your furnace” alerts and it’s stressing me TF out.


r/ecobee • • 3d ago

PEK install issues with AC. Tech support couldn’t help.

Thumbnail
gallery
3 Upvotes

Hi All, I called my AC guy to install an Ecobee Premium and the PEK. Well they messed up slightly because the thermostat had an error. Ecobee tech support helped me fix the error and the heater worked. But the AC now doesn’t turn on the condenser so it just blows regular air. Ecobee tech support said everything was connected correctly.

Can anyone tell me what’s wrong here so I can save a few bucks? Thank you!


r/ecobee • • 3d ago

Problem AVOID HELLOTECH FOR INSTALLATIONS

2 Upvotes

I'm writing this as a warning for anyone wanting to outsource the installation.

Had a guy come yesterday to install it. Had some issues. He doesn't even install the adapter despite not having a C-Wire and installs another transformer. He asked for 40 bucks in cash for that part, which was strange, but I stupidly went with it, because when he turned it on it appeared to be blowing air. It was high 60s yesterday, so heat appeared on and working.

Well, the heat wasn't working after:

- 2-3 hours talking to ecobee support

- 2 hours with an electrician

I come to find out that the guy put a shorted wire somewhere that would require 1500 of rewiring and there was no reason for the transformer to be installed due to my boiler set-up.

I called HelloTech 4 times, messaged them quotes and the transcript from support that said this was done wrong. It's 30s outside and they need to do a 1 to 2 day investigation. And if the guy doesn't follow up, it's another 1-2 days they give him.

They offered no other options. I'm hosting Thanksgiving, so coughing up the $1500 to rewire my apartment. This has been such a stressful experience. The electrician also said he's seen the most problems with these.

I'm sure HelloTech has excellent attorneys.


r/ecobee • • 3d ago

Ecobee Essential wanting to add a wood boiler

Thumbnail reddit.com
1 Upvotes

r/ecobee • • 3d ago

Ecobee Essential wanting to add a wood boiler

1 Upvotes

I have an Ecobee home essential thermostat controlling a traditional split system (gas furnace and an AC compressor and A coil). All is functioning well. I have added an outside wood boiler with circulating pumps that run 24/7 and a water to air heat exchanger in the plenum of the central HVAC system. Now am down to wiring and can not find a clear answer on Ecobee website or owner's manuals. I want the heat exchanger to be primary and the gas furnace to be secondary heat source.

Currently I have the following wires on my thermostat. R - Red wire (power), C- Blue wire (common), G - Green (fan), Y1 - Yellow (cooling), W1 - White (heat)

My thinking is just move the G - Green (fan wire) to W1 and move the W1 - White (heat) wire to OB (currently empty). My questions are: 1) Will this interfere with the AC operation in the summer?

2) What triggers the thermostat OB terminal? 3) Will I need to reconfigure anything on the thermostat options?

I appreciate your responses. Thanks!


r/ecobee • • 3d ago

Configuration New to Ecobee and can’t for the life of me figure out Eco Mode.

5 Upvotes

Today I was at home for a couple extra hours after my system was scheduled to go into “Away” mode. Despite my sensors reading occupied in the three rooms I was active in, eco mode never kicked the system on because it noticed someone was home.

A few hours later I was at work and checked the app to find that eco mode had kicked the system in because it sensed someone was home. There was one sensor in my bedroom showing occupied despite no one being home.

The sensor is in a place where it doesn’t get light or airflow or anything else they say can cause it to read as occupied. But even aside from all that, it’s weird that a single sensor detecting a presence turned the system on but three did not.

What gives? I wanted to allow the system to learn in order to heat my home as effectively and efficiently as possible, but am I better off just shutting off Eco mode altogether?


r/ecobee • • 3d ago

Configuration House Thermostat Controlling Second Heater

0 Upvotes

I have a premium thermostat, have a heat pump, furnace, and humidifier (which I don't think is currently configured).

I have a non-heated room that I want to add a space heater to. I want this zone and heater controlled on a different schedule.

Do I need to buy a second thermostat or can I somehow configure this? I can figure out the wiring, if the software functions exist


r/ecobee • • 3d ago

Ecobee Premium thermostat, 2 stage Carrier furnace/AC and manual bypass humidifier.

Thumbnail
gallery
1 Upvotes

A local HVAC company installed our Ecobee while doing maintenance on our Carrier 59TP5A. Our furnace is a two stage unit but the Ecobee is only tracking it as a single stage. Id also like to put our Aprilaire 500M under the control of the Ecobee. We have the older 4 wire but I can easily run a 18/8 wire due to this place being a ranch and everything is easy to get to. Im just a bit confused on the wiring with ACC + and PEK+ ect. ect. Any help is appreciated.


r/ecobee • • 3d ago

Problem Smart sensor won’t pair

1 Upvotes

Hi All,

I have a total of 4 smart sensors and 2 thermostats.

One smart sensor is paired with the upstairs thermostat.

Two smart sensors are paired with the downstairs thermostat.

I am trying to get the last smart sensor to pair with the upstairs thermostat but it simply will not take it.

It pairs immediately to the downstairs thermostat, so I suspect there isn’t anything wrong with the sensor itself.

I’ve tried rebooting the upstairs thermostat by removing from the wall for a few minutes, I’ve reset the sensor by removing battery for a few minutes, all of the troubleshooting steps on the ecobee help page. Still won’t pair with the upstairs thermostat.

I’ve wasted a considerable amount of time troubleshooting this issue with the same results.

Anyone have any tips or insight? Sounds like a software bug to me and Ecobee support has not responded to my email about this issue (not sure if that is surprising, this is my first issue and I’m a new user).


r/ecobee • • 3d ago

Consistently blowing out cold air

Thumbnail
gallery
0 Upvotes

First image is my old thermostat that works perfectly. I’ve energized both on heat and on cool and it still blows out cold air. Any and all suggestions would be appreciated. Thank you for your time!


r/ecobee • • 3d ago

Monthly Reports

2 Upvotes

The monthly reports haven’t updated in the app since July. Is it an Ecobee issue or a setting issue?


r/ecobee • • 3d ago

Can't login

Post image
0 Upvotes

Maybe the logged in experience is just down?!


r/ecobee • • 3d ago

Configuration PSA: "Away" profile does not use your master thresholds/differentials - it adds 1.0F or 0.6C

1 Upvotes

I know this has been mentioned here before, but I want to put it in front of people because I have been fighting this for the past few weeks and only just learned the cause.

My wife is on maternity leave and home all day, and instead of changing the schedules for my comfort profiles I decided it was easier to just change the set point for the Away profile. The theory being that when she goes back to work I'll just change the Away temp back to what it was instead of having to mess with schedules again.

As the weather has gotten cold we've been confused as to why the house feels cold in the morning when the Away profile is in effect, but normal in the afternoon when the Home profile is working. They're both set to 70F and they utilize the same sensors. Manual temperature holds worked fine. Manually holding the comfort profile to Home worked fine. But when it was on Away per the schedule, the house was cold.

My differential is set to 1 degree, so I expected the temperature to fall to 69F, then the heat kicks on to get it to 70F and then the cycle repeats. Instead, the temp was allowed to fall to 68F before the heat would kick on. And since this profile is averaging two sensors, it's actually allowing the colder sensor to get as low as 66 point something while the warmer sensor was 68 point something until the average fell below 68.

This +/- 1F (0.6C) override to your thresholds also applies to custom comfort profiles if you check the box for "no one is usually home." This also applies in cooling mode - so if it's set to 72F Away with 1F differential, the house can get as warm as 74F before the air conditioning turns on.


r/ecobee • • 3d ago

Problem What's the trick to get this to connect to wifi?

Thumbnail
gallery
0 Upvotes

I have an Ecobee Smart Thermostat Premium. Its been going fine since I installed it in 2023. However, today I realized it was offline. Ive tried reconnecting it to wifi and it wont connect.

My unifi access point is literally right above the thermostat, so its in range.

I have 3 ecobee thermostats and the other two are connected fine.

The wifi radio is enabled.

I pulled it off the wall to reset it and now its saying the password is incorrect, even though that is not the case.

Any ideas?